AT my plant it is purely for testing. Here it works like this: LOCA: diesels auto start but do not pick up safety busses (just in standby). LOOP sequencers strip the bus close the output breaker and sequence on loads. If paralelled for testing output breaker opens and either of the above happens (depending on LOCA or LOOP) only reason to synch to the grid is to load it down for testing (monthly) safety loads are only about half of the 6MW output per diesel
I wish my plant had diesels this large. We are only good for about 2600 KW for continuous running. We are limited by what we can change due to margin on the diesels.
We consider the diesel INOP and unavailable while it is tied to the grid. We did a mod on it recently to allow it to remain operable during testing but there are still issues that need to be resolved. Anytime we do something with the diesel, I automatically perform a 3.8.1 Condition B surveillance check so we don't get hit for missing the 1 hour action.
If there is a LOOP while the diesel is tied to the grid, the output breaker and bus tie breaker open. The undervoltage will strip all loads with the exception of the CCW pump and the 4160 V to 480 V transformer. When the EDG output breaker recloses on the bus, the CCW pump instantly restarts if it were running before the undervoltage and 10 sec if it were not running before the undervoltage. The Makeup Pump (similar to the Charging pump only centrifugal and higher capacity) restarts 2.5 sec later if it was previously running. The service water pump (similar to a river water pump) restarts 21 seconds later.
If there is a LOOP and SFAS signal, the SFAS sequencer kicks in. There is a start signal to the ECCS pumps depending on the SFAS Level that the SFAS sequencer will block, unblock for 3 seconds, and reblock the loads until the sequencer has finished its run time (about 25 seconds). The sequencer only blocks HPI, LPI, Service Water, and CTMT spray (unblocks in this order). The CCW pump will get an auto start on the SFAS and closes regardless of voltage. The only thing that will stop the CCW breaker from closing is a Lockout.
We also have a Blackout diesel and it is bigger than the EDGs. We have to manually start it and it has to go through a nonessential bus if we want to power an essential bus.