Power Reactor Event Number: 49106
Facility: FARLEY
Region: 2 State: AL
Unit: [1] [ ] [ ]
RX Type: [1] W-3-LP,[2] W-3-LP
NRC Notified By: WILLIAM ARENS
HQ OPS Officer: CHARLES TEAL Notification Date: 06/12/2013
Notification Time: 01:33 [ET]
Event Date: 06/11/2013
Event Time: 21:05 [CDT]
Last Update Date: 06/12/2013
Emergency Class: NON EMERGENCY
10 CFR Section:
50.72(b)(2)(iv)(B) - RPS ACTUATION - CRITICAL
50.72(b)(3)(iv)(A) - VALID SPECIF SYS ACTUATION
50.72(b)(2)(xi) - OFFSITE NOTIFICATION
Person (Organization):
FRANK EHRHARDT (R2DO)
Unit SCRAM Code RX CRIT Initial PWR Initial RX Mode Current PWR Current RX Mode
1 A/R Y 100 Power Operation 0 Hot Standby
Event Text
UNIT 1 AUTOMATIC REACTOR TRIP DUE TO THE LOSS OF A START-UP TRANSFORMER
"This is a report of an automatic RPS actuation and automatic ESF actuation per 10CFR50.72(b)(2)(iv)(B) and 10CFR50.72(b)(3)(iv)(A). Additionally, this is to report intentions for a press release per 10CFR50.72(b)(2)(xi).
"At 2105 CDT on 6/11/13, Farley Unit 1 experienced an automatic reactor trip from 100% power. The initiating event was the loss of the 1B Start up Transformer which resulted in de-energization of the B-Train ESF 4KV buses and the 1B and 1C Reactor Coolant Pump Buses. The 1B Emergency Diesel Generator auto started and tied to the B-Train 4KV Emergency buses.
"Both MDAFW (Motor Driven Auxiliary Feedwater) Pumps and the TDAFW (Turbine Driven Auxiliary Feedwater) Pump auto-started and are supplying AFW flow to the steam generators. Decay heat removal is via the steam dumps to the main condenser.
"The cause of the loss of the 1B Start-up Transformer is unknown and is currently under investigation. All other systems functioned as expected in response to the loss of the 1B Start-up Transformer and reactor trip.
"The NRC Senior Resident Inspector has been notified.
"A press release is planned."
All control rods fully inserted. There is no impact on Unit 2. Currently the licensee does not plan to restart the 1B and 1C Reactor Coolant Pumps. Pressurizer spray has been isolated from the 1B loop per procedure. Main Condenser vacuum is adequate for decay heat removal.