This Confirmatory Action Letter (CAL) confirms that SONGS Unit 2 will not enter Mode 2, and SONGS Unit 3 will not enter Mode 4 (as defined in the technical specifications), until the NRC has completed its review of your actions listed below. The permission to resume power operations will be formally communicated to you in written correspondence.
Actions for Unit 2
1. Southern California Edison Company (SCE) will determine the causes of the tube-to-tube interactions that resulted in steam generator tube wear in Unit 3, and will implement actions to prevent loss of integrity due to these causes in the Unit 2 steam generator tubes. SCE will establish a protocol of inspections and/or operational limits for Unit 2, including plans for a mid-cycle shutdown for further inspections.
2. Prior to entry of Unit 2 into Mode 2, SCE will submit to the NRC in writing the results of your assessment of Unit 2 steam generators, the protocol of inspections and/or operational limits, including schedule dates for a mid-cycle shutdown for further inspections, and the basis for SCE’s conclusion that there is reasonable assurance, as required by NRC regulations, that the unit will operate safely.
Actions for Unit 3
3. SCE will complete in-situ pressure testing of tubes with potentially significant wear indications in accordance with the Electric Power Research Institute (EPRI) Steam Generator In-situ Pressure Test Guidelines and will plug tubes in accordance with those guidelines.
4. SCE will plug all tubes with wear indications in excess of your Steam Generator Program Requirements (SGPR) and EPRI guidelines as well as perform preventive plugging or take other corrective actions to address retainer bar-related tube wear in Unit 3.
5. SCE will determine the causes of tube-to-tube interaction and implement actions to prevent recurrence of loss of integrity in the Unit 3 steam generator tubes while operating.
6. SCE will establish a protocol of inspections and/or operational limits for Unit 3, including plans for a mid-cycle shutdown for inspections. The protocol is intended to minimize the progression of tube wear, and ensure that tube wear will not progress to the point of
degradation that could cause tubes not to meet leakage and structural strength test criteria.
7. Prior to entry of Unit 3 into Mode 4, SCE will submit to the NRC in writing the results of your assessment of Unit 3 steam generators, the protocol of inspections and/or operational limits, including schedule dates for a mid-cycle shutdown for further inspections, and the basis for SCE’s conclusion that there is a reasonable assurance, as required by NRC regulations, that the unit will operate safely."